Question
01/05/12

anologue programmer

A question regarding P10059278 (Glow-worm Ultracom2 24 CXI Condensing Combi Gas Boiler (NG or LPG))

if i fit a anologue programmer do i have to fit a room stat.
have tried to fit programmer but boiler will not work unless i take out link in boiler. then if i do this it will not work unless i fit a room stat is this right.



Answer
Hello Mick,

Thank you for your enquiry.

you really need to fit a room stat otherwise your boiler will run constantly until the programmer turns the heating off.

Your easiest option would be to fit a wireless programer/stat/

Regards

Phil